What is the logic behind bonding your lightning ground to the house ground? Lightning always wants to go to the earth, so grounding your antenna and coax makes sense. You give the lightning an easy path to the earth, and hopefully it will take it. I also understand why it's recommended that you bond the common ground for your equipment to the house ground. The powered equipment is part of the same circuit as all the other electrical equipment in the house and you want to keep it at the same potential. However, I don't follow the reasoning of bonding the two together. It seems to me that the most logical solution for protecting against lightning is to give the electrical buildup a way to get to the earth without directing it into your house; i.e., a lightning ground separate from the equipment ground. Yet everything I read recommends bonding the lightning ground to the house ground, so there must be some reason that I don't understand.
You can post now and register later.
If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.
Question
WRTC928
What is the logic behind bonding your lightning ground to the house ground? Lightning always wants to go to the earth, so grounding your antenna and coax makes sense. You give the lightning an easy path to the earth, and hopefully it will take it. I also understand why it's recommended that you bond the common ground for your equipment to the house ground. The powered equipment is part of the same circuit as all the other electrical equipment in the house and you want to keep it at the same potential. However, I don't follow the reasoning of bonding the two together. It seems to me that the most logical solution for protecting against lightning is to give the electrical buildup a way to get to the earth without directing it into your house; i.e., a lightning ground separate from the equipment ground. Yet everything I read recommends bonding the lightning ground to the house ground, so there must be some reason that I don't understand.
Top Posters For This Question
17
10
6
5
Popular Days
Jun 28
15
Jun 29
15
Jun 30
12
Jul 4
4
Top Posters For This Question
WRTC928 17 posts
SteveShannon 10 posts
WRKC935 6 posts
LeoG 5 posts
Popular Days
Jun 28 2025
15 posts
Jun 29 2025
15 posts
Jun 30 2025
12 posts
Jul 4 2025
4 posts
Popular Posts
WRXL702
It's Called Single Point Grounding. Reason - To Eliminate A Potential Difference Between Having (2) Separate Grounding Systems. Single Point Grounding Is Done On All Commercial Tower Sites.
WRKC935
Another, and a bit more in depth explanation / fact with lightning grounding and bonding. And the reason you ground EVERYTHING. Wires are NOT a perfect conductor. No matter the wire size or len
WRYZ926
I have bulkheads through the wall to bring the coax in. I also have a metal plate on each side of the wall with a piece of 1/4" 20 all thread through the wall that I use for my ground point. I have a