  • 2
Question re: grounding for lightning protection
What is the logic behind bonding your lightning ground to the house ground? Lightning always wants to go to the earth, so grounding your antenna and coax makes sense. You give the lightning an easy path to the earth, and hopefully it will take it. I also understand why it's recommended that you bond the common ground for your equipment to the house ground. The powered equipment is part of the same circuit as all the other electrical equipment in the house and you want to keep it at the same potential. However, I don't follow the reasoning of bonding the two together. It seems to me that the most logical solution for protecting against lightning is to give the electrical buildup a way to get to the earth without directing it into your house; i.e., a lightning ground separate from the equipment ground. Yet everything I read recommends bonding the lightning ground to the house ground, so there must be some reason that I don't understand.
49 minutes ago, WRTC928 said:
How does it change the calculations if the antenna is mounted on something non-conductive like a fiberglass mast?
Obviously you don’t ground a fiberglass mast, but your coax shield is attached to part of the antenna somewhere and it will develop a charge as air currents pass over it.
Now the difference in potentials is between the metal parts of the antenna connected to the shield of the coax and the service ground, again going through your equipment and possibly you. One of the purposes of a surge suppressor (commonly called a lightning protector but nobody guarantees that) is to allow you to bond the coax shield to the grounding system.
22 minutes ago, tcp2525 said:
All radio related grounding should be done with 500MCM cable. End of story.
I'm sorry, but I don't understand how that relates to my question. Please elaborate.
The actual ground (i.e., dirt) can be a conductor of lightning that hits nearby, especially wet ground in a thunderstorm.  By installing grounding wires, you may be increasing potential of that getting to your electronic devices inside.  For ordinary folks, disconnecting the devices from the AC and antenna lines is the best option.
2 hours ago, WRXL702 said:
It's Called Single Point Grounding.
Reason - To Eliminate A Potential Difference Between Having (2) Separate Grounding Systems.
Single Point Grounding Is Done On All Commercial Tower Sites.
Yes, but commercial tower sites don't then bond the ground to a house ground. What I'm trying to figure out is why almost every article or video I find recommends doing that.
That was my logic, hence my confusion at the recommendation to do that.
Correct - Because Commercial Sites Don't Have A House - They Have A Structure Or A Cabinet For Equipment.
The Structure Or Cabinet Requires Proper Bonding - For Single Point Grounding - To Avoid A Ground Potential Difference.
To prevent electrical noise being transferred from one system into the other system. You are drawing power from one electrical system thus you should be using only one grounding system. If you have two earth grounding points then you have two grounding systems and that will cause problems.
I'm not following you. What does that have to do with lightning protection? What kinds of problems will it cause?
To be clear, I'm not being confrontational. I'm really trying to understand this.
Let’s disregard lightning protection for a few minutes and just talk about bonding to your house service ground.
Your tower is sort of grounded. We all agree with that I think. It’s embedded in an imperfect conductor, concrete, at the bottom. To improve the grounding a ground wire runs from each leg of the tower to a ground rod. But any two separate ground rods are almost always at different potentials. Whenever you have different potentials between two points in a circuit you will have electric currents flowing from one point to the other. So, the three or four legs of the tower are bonded together using a material that is more conductive than the tower itself. Otherwise you have current flowing between the legs of your  tower. If current flows between the legs of your tower over time the metal of the tower will corrode. Bonding between the three or four legs provides an easier path for the current to flow which keeps the legs all at the same potential.
In addition your antenna mount is certainly connected electrically to your tower and your coax shield is connected to your antenna mount. Your coax shield then runs to your radio. If you have a watt meter, amplifier, or any other device between your radio and your antenna, they are all connected serially via the coax shield. Their metal cases are all connected to the coax shield. So all of the devices in your shack are connected together via the coax shield. If a power surge comes through the shield (static, lightning, unicorn farts, whatever) it is going to cause current to flow through your equipment because that’s the most direct path. By bonding the chassis of all those devices to a single point, we provide a much better path that doesn’t flow through those devices. So that’s why we use a single point ground. But remember, that single point ground is connected to ground at the tower.
You power your radio with a power supply that’s plugged into your house power. Its case is connected to the ground wire in the outlet which runs back to the service panel where it’s bonded to the service ground for the utility power coming into your house. It has to be because NEC says so.
So let’s say you don’t have your single point ground bonded to your service ground. You reach out to touch your radio and at the same time your brush your other hand on the power supply. The potential of your tower ground, which is what your one hand is touching, is probably different than the potential of the service ground, which is what your other hand is feeling. And it’s DC. Your heart can be stopped by as little as 1/10 of an ampere. So you die.
So we bond the tower ground to the utility ground to ensure they are at the same potential and save your life.
Also with fewer ground currents in the shack we hear less noise.
18 minutes ago, AdmiralCochrane said:
So, a home antenna tower shouldn't have it's own ground? Just bond to house ground?
Unless I misread the NEC and other sources, the tower should have its own ground and be bonded to the service ground.
This is correct.
Steve did a good job of expelling things
It's no different than using a chimney mount or a satellite dish mount on your roof. You run the proper sized ground wire from the antenna/mount to ground.
Look at a properly installed satellite dish antenna. There will be a ground wire running with the coax. And that ground wire should be bonded to your service ground before the coax enters the structure. The same goes for cable TV, there will be a ground wire coming off the feed  to your home and it to will be grounded to the service ground when installed correctly.
To explain it really simple.
If you have a ground rod on one end of your house for your service and another one at the other end of the house with your radio gear and they are not bonded together.  If you have a strike, even a ground strike at one end of the house, a tree near the house, or whatever at that end.  The lightning will COME IN the one ground, go through your equipment via the safety ground (bottom pin on power cord) across the equipment / power supply, into the radio then back out to the coax or ground wire, then out to the ground rod it's all hooked to.  That is the difference of potential that is talked about.  The ground is NOT a perfect conductor.  And it's not unreasonable to see 50 Kv or more across 10 feet of ground during a strike.
I install public safety radio sites, including ones that are co-located dispatch centers with radio towers.  Key part of this is the dispatchers wear headsets that as far as lightning goes, a direct path exists between the top of that tower and their headsets.
You BOND everything.  The headset jack gets bonded, the furniture, the equipment, the racks the equipment is in, the radios, the wiring between the radios and the console electronics, the coaxes entering the building with a surge suppressor, then outside the building, at the base of the tower, every 100 foot up the tower and then right at the connection point to the antenna.  The tower gets bonded to all this.  Then there are ground rods on every leg of the tower.  Those are bonded together, called a tower ground loop.  Then the building has a ring around it with ground rods every ten feet again in a loop.  Those rings are bonded together, there are lines that go out into the property with more ground rods that are every 10 feet.  All the connections are done with CadWeld or 15 ton compression connections with a hydraulic press.
All that is bonded to the service entrance ground.
Then in the building, everything that is metal that is a fixture gets grounded.  Meaning file cabinets, conduits, desks, window and door frames.  Anything that not immediately movable.  Of course, air handlers, plumbing, and the like are also bonded back to the ground along with the building frame if it's conductive.
A lot of people will question the required wire gauge, stating that a number 2 wire could never hold the current of a direct strike.  And that's only partly true.  Lightning is very fast.  Wire will carry a very high amount of current for a very short amount of time.  Anyone that's ever shorted something across a battery will recognize that whatever it was didn't instantly turn to plasma and vanish.  It takes some time for the wire to heat up and then catch fire.  And longer for it to burn in half.  It's that fact that allows a number 2 conductor to take the abuse of being hit across and not just being vaporized.
Yes, there are instances that heavier wire is needed.  Like the ground rings, runs longer than 50 feet and situations where a multipoint grounding bar is located where a number of devices are connected to a single point with number 6 wires.  But a number 6 wire, at least with the R56 install standard, is the minimum required wire gauge for any ground and if it's connected to a ground bar with other devices or grounded objects, then the wire going from that ground bar back the the master / main ground bar needs to be a number 2.
OH, and what you are referring to as a 'house ground' is the electrical service ground.  And at a tower site it IS bonded to the site grounding system.
Google the R56 standard and read over the site grounding requirements for a tower site.
Okay, now it makes sense.
So why isn't the tower bonded to the electrical ground through the coax which is attached to the chassy which is grounded through the ground line in the power outlet?  No matter how much you ground anything because of the resistance of wire they'll always be at a different potential?
Because the ground line of the power supply is isolated from the plus and minus 13.8 vDC lines that provide power to your radio or DC power distribution box.
8 hours ago, WRXB215 said:
Very good explanations in this thread.
Ground because lightning.
Bond because potential.
Disconnect/open loops because EMF.
Lightning strike between my house and neighbor's house took out 2 window AC's and 3 TV's at the neighbor's house, but just a light ballast and the power filter board on my HF rig.  If I had had the HF rig disconnected from the power supply it would have just been the light ballast.  Power poles are your friend.
Another, and a bit more in depth explanation / fact with lightning grounding and bonding.  And the reason you ground EVERYTHING.
Wires are NOT a perfect conductor.  No matter the wire size or length, copper wire does have a resistance.  Meaning that a voltage applied at one end of the wire will NOT be the same as the voltage at the other end of it depending on the voltage and current in the wire.
More over, and this was mentioned before.  The ground,  no matter the number of rods, plates, screens or whatever you bond together in your grounding field. That connection to the ground is NOT perfect either.
So, when a strike happens, a direct strike.  The voltage (potential) of the equipment with reference to earth ground (0 volts) rises with the strike and then falls.  Now this can be thousands or possibly tens of thousands of volts.
So, that being said.  If you DON'T bond everything together and the tower takes a strike.  The radio is connected to the tower.  The power supply is connected to your safety ground for the utility feed.  Between them is a potential voltage of thousands to tens of thousands of volts.  The radio and the power supply are sitting next to each other and the radio case voltage is 50KV, and the power supply case potential is 0 volts.  Guess what happens.  Bang. Flash. Smoke.
If everything is bonded, it all goes to 50KV or whatever voltage, and then back to zero.  And you are protected from that spike.  Because it all went up and down.  It's the difference in potential that causes issues.  And a crappy ground field and good bonding practices are far SAFER than a great grounding system and half the gear not being connected to it, and in truth, its worse than nothing at all because it really creates the possibility of the difference in potential in the radio room.
Now, no one has discussed the reason we ground to begin with.  And the primary function is NOT to handle a strike.  That's a secondary function.  The primary function of a grounding system is to keep everything connected to it at ground potential and at 0 volts with reference to ground.
The CB guys will tell you about their coaxes popping while they are in a glass jar and disconnected from the radio.  This is the MOST DANGEROUS situation of all.  Reason being is that antenna is going far above ground potential by thousands of volts until the air breaks down as an insulator and it arc's off.  Lightning will always take the path of least resistance.  To understand that, you need to understand the whole 'potential' thing.  The short version is that lightning will strike the place that has the highest charge on it.  If your antenna has several thousand volts on it and the tree next to it don't and the ground don't then boom, the antenna gets the hit.  The higher in the air something is and the higher the potential that thing has, is gonna be the point that the strike happens.
So then we introduce grounding and bonding to the mix.
When you ground the tower, feed line, antenna, obstruction light, and all the rest of it.  All of it's at the same potential as the ground that it's sitting on / in.  All that static build up, which is what causes the coax to arc off in the storm, is run to ground and that keeps the potential low.  For the radiating elements on a non-grounded antenna like a long wire or a dipole for HF work, a surge suppressor is used.  And they have multiple things internally that help keep the potential low.  First is a resistor that has enough resistance to NOT effect the SWR or impedance of the antenna system.  Now the second part is a gas discharge tube.  These tubes are rated to 'fire' or short when a voltage above a certain point is reached.  This is where the power or wattage rating comes from on these.  Because we know the resistance / impedance of the circuit (50 ohms) the voltage across that 50 ohm load will result in some power level.  So the firing voltage is some percentage above that voltage.  It's why hams running mismatched antenna's will fire their surge suppressors when running reasonably low power levels but the antenna instead of being 50 ohms is 700 ohms or something like that and they are using an antenna tuner to lie to the radio and show it a 50 ohm impedance.  The impedance doesn't change in the antenna and cable past the tuner, it's still high.  THe tuner is what matches it.  BUT, 100 watts is 100 watts. IF that's what you are putting into the antenna when it's operated in it's bandwidth and presents a 50 ohm impedance then the voltage is X.  But if the antenna is 700 ohms and the power is still 100 watt's the voltage is NOT X any more, it's far higher.  And that surge suppressor will fire at that point.
But back to the point of keeping everything, but mostly the tower, at ground potential is this.  If the top of the tower is the same potential as the ground around the tower, then the lightning will go find a tree somewhere to hit.  Or it will hit the ground because the top of the tower doesn't look any better to lightning than the ground around it.  Don't bleed off that static charge and that tower will take hits.
And a tower that's been hit a couple times will get to the point it looks REALLY good. Reason is that the ground rods will encase themselves in glass or whatever dirt is around them as the get hit.  The more often they get hit, the more buildup happens.  In sandy soil, they will encase themselves in glass.  And at that point you have no more ground.  The whole system will need to be dug up and replaced.  I have seen this.
That right there should protect the radio.  But I know nothing will protect with a direct hit.  Dissipating charge should be accomplished with the wire sizes as they are.
I'm just thinking about my situation.  The main electrical connection to all 4 bays in the building I'm in is at the opposite side of where my antenna is.  That's 170' of conductor needed to make the connection from where the cable enters the building to the bond where the electrical box is.  25'+100'+45'.
And as to having a ground rod for each leg of the tower why can't the 3 or 4 legs be connected by copper wire and then go to a single ground rod?  The ground loop around the tower is doing essentially just that but just increasing the cost substantially.  And would that change between a steel tower and an aluminum tower since aluminum conducts better?
Lighting is just like tornadoes.  Destroying one while barely touching the one next door.  Could have been grounding, or just dumb luck.  People struck by lighting can survive or become crispy kritter piles of dust.
Yes, there is always going to be a difference.  You bond because coax connectors are NOT high current rated. The circular mills of the shield conductor is also not sufficient to minimize the resistance of the conductor.  This is why you don't use split bolts and crap to do your grounding.  It's all CadWeld or 15 ton compression lugs / connections.